Better late than never, but I want to put in my 2c about the 15A outlet subject from a sparky's perspective!
The earth prong is larger purely to stop a 15A appliance being plugged into a 10A outlet. A short to earth in a 15A device will have the same fault current as a short in a 10A device (for the purpose of this discussion), so it's nothing to do with that. A 20A plug/socket has enlarged active and neutral pins. You can still plug a 10A appliance into a 20A outlet, but a 20A appliance won't fit in a 15A outlet.
A 15A outlet can be installed on a circuit run in 2.5mm2 as 2.5 will usually support up to 22A, and a 16A breaker is recommended, but 20A can be used. It depends on the way the circuit is run, your sparky will make the judgement. 4mm would usually only be required for a long run such as a single circuit being run to a back shed from a front switchboard.
Only one 15A outlet can be installed per 16/20A circuit (each 15A outlet is woth 15/12A respectively for circuit loading calculations), and being a socket outlet the circuit must be RCD protected! The only way around the RCD rule is to hardwire the welder, which defeats the purpose of portability if required
And please NEVER file down the earth pin or fit a lower rated plug!!!!